A solution for the design and verification of fire safe rigid joints between concrete members constructed using post-installed rebars


1.0K

Fire disasters happen frequently everywhere in the world, and fires are an unfortunate reality that can occur on all types of structures, thus being a significant risk to lives and assets that might lead to grievous casualties.

During the event of a fire, structures can typically resist the heat for some time, but if the fire duration extends long enough, it impacts the stability of concrete structures with the eventual consequence of complete or partial collapse. Hence fire safety is of critical importance and an essential requirement that all structural building codes globally prescribe through mandatory fire resistance durations for structural elements and systems, including their connections. This helps ensure enough time for occupants to evacuate, for rescue activities to be completed, and for the fire to be safely extinguished.
 


Building codes generally provide guidance to design traditional reinforced concrete systems. Unfortunately, most codes do not provide sufficient guidance to ensure fire safety when using non-traditional solutions, such as post-installed rebar systems. In these cases, it is the responsibility of the structural engineer to ensure building structures meet the code-mandated fire resistance to meet the mandated requirements through expert considerations and engagement with specialist solution providers.
 
Post-installed reinforcing bars (rebars) are an effective solution on most job sites to connect concrete members cast at different times. This solution is nowadays widespread in both existing constructions, e.g., for strengthening or refurbishment needs as well as in new buildings, e.g., to optimize the construction process or correct design/construction mistakes. These structural connections shall be designed to resist various types of loading including static loading, seismic actions, and fire exposure. However, the design of rigid joints with post-installed rebars under fire exposure is not covered in state-of-the-art codes and guidelines.  Because of this, Hilti being a leader in the industry toward safer buildings, provides solutions by developing hardware, design methods, and design software that help ensure a fire-safe built environment.

Background
Post-installed rebar connections in concrete can be used to extend a structural element using lap splices (e.g., slab extension, wall extension, etc.) and in some cases to ‘simply support’ an element onto another (e.g., slab onto a wall). However, end anchorages using post-installed rebars are often required to enable rigid connections of one structural member to another which are usually perpendicular in direction to each other (e.g., column/wall arising from foundations, a beam onto a column). The scope of such post-installed rigid moment-resisting joint applications is limited by the design method following provisions of the Eurocode EN 1992-1-1, where such rigid joints are usually designed and executed as lap splicing. This is not always a feasible solution since in many cases the members are already constructed, and the new members are to be post-installed.
 
EOTA has developed a post-installed reinforcement (rebar) design technical report (TR) 069 where the structural elements that are experiencing bending moments can be designed without the need for a splice configuration in the existing member. The design method extends the design range of applications which now includes end-anchorage connections for rigid joints in concrete structures.  

 

EOTA TR 069 considers possible different modes of failure such as steel yielding, concrete cone failure, resistance to pull-out, and splitting failure, which is a holistic and straightforward approach towards verifications based on anchor theory (which takes into account the tensile resistance of concrete in the breakout verification) without the need for the assumption of rebars being anchored only in confined zones. Furthermore, the product-dependent bond strength of the specific post-installed rebar system is considered via assessment according to the EAD 332402, which is much higher than Eurocode limitations.

Limitations in fire design for rigid nodes

In the European code and design framework, the splice connections and anchorages in simply supported connections can be designed for fire following the provisions of EN 1992-1-2 and EN 1992-1-1. While EOTA TR 069 allows for the design of post-installed, moment-resisting rigid joints in reinforced concrete connections under static loading and seismic loading conditions, unfortunately, it does not include design provisions when exposed to fire action. This limitation of the design method has been a pain point for engineers in encompassing all the design actions while providing a complete solution. 



Solution for fire safe design of rigid joints – Hilti method
To bridge the gap of non-availability of fire design of rigid joints using EOTA TR 069 investigations on the bond-splitting behavior of post-installed rebars at elevated temperatures were conducted (see test setup and specimen images below). As a result, the new Hilti method for fire design of rigid joints was formulated as a smart design approach that utilizes the design strength verification equations for failure modes from EOTA TR 069 with few meticulous modifications. A key parameter is the reduced bond strength in terms of the reduction factor of the chemical mortar under fire exposure from the relevant ETA published as per EOTA EAD 330499-02-0601 which is used for bonded anchors.

Design flow
For the fire design of rigid nodes using this design method, the following steps are applied: